I got these instructions from overkill solar.. gonna try these steps now.
I have a couple comments /questions
I have a couple comments /questions
- you can start by disconnecting the B- on the BMS from the cells and the balance line harness, let the BMS power down (10 seconds) and reconnect. May or may not be needed.
- I think you have a loose balance lead that's why the voltage is jumping all over. Take a look at the pic below, you should change the balance lead ring terminals they are too big for the bolts you are using (or maybe put them underneath like on cell 4)
- Also I would recommend changing out the terminal bolts you are using with a stud and nut pic below. (as long as you are going to the hardware store for smaller ring terminals) We find that the bolts can bottom out in the cell and even though it feels tight it is not. I do see you are using multiple nuts below the crew head so you may be ok but not great.
- did you top balance the cells?
- I see one screen shot where all the cells are at 3.307 ( I am guessing first reading from the factory?)
- the Dr meter is a bench power supply? I am guessing its ok, You could use this , once the connection issue is resolved, to get the battery near full, but you will want to top balance at the end .
- I would change the Cell minimal voltage from 3000 to 2500. these numbers are used by the BMS to calculate SOC nothing else. The protection #s will stop/start the BMS.
- I would also change the Cell % Cap. voltage #s to match your cells SOC chart. If one did not come with your cells I would start with a straight line 3350,3300,3250,3200.