My EPEver Tracer manual says 5amp per mm2I'd be also curious to have some expert's opinion on this. The only rule of thumb I found is 1.4 x area in mm2 for copper. That would make 56Ah for a 40mm2 section ?
I would be very hesitant to put that kind of current through this small of a bus bar. I don't doubt that it will handle it, but there will definitely be a temperature rise."Copper Busbar Rating - Austral Wright Metals -" https://www.australwright.com.au/technical-data/advice/copper-busbar-rating/
Yea...I'll perhaps take time tommorow to get the formula to calculate all this. We also got to keep in mind that it's very short and length is an important factor. In fact you can put lot of amp in a wire...it will just heat, then finally burn if it can't dissipate ....a lot of energy could be lost in this heating....That doesn't sound right to me.
I'm not well versed in calculating Busbar Ampacity but:
The dimensions shown are 2mm x 20mm (40 mm²)
I can't find a good metric ampacity table so this one will have to do
The smallest busbar on that list 1/8" x 1/2" is also roughly 40 mm²
and is rated for only 150A DC
For reference 40 mm² = 79,000 circular mils = a cross section in between 2AWG and 1AWG
Maybe someone with more knowledge than me clarify, but based on the above I would not trust those busbars to carry anywhere near that much current safely.
I believe we are talking about battery busbars here, so they will definitely not be in open air with nothing of consequence around.If your bus bars are out in the open with nothing combustible anywhere near, you are probably fine. I wouldn't put it in an RV or my house.
I'd be also curious to have some expert's opinion on this. The only rule of thumb I found is 1.4 x area in mm2 for copper. That would make 56Ah for a 40mm2 section ?
So how much current was going through those bus bars? If those measurements are accurate, please give us a figure of Amps per mm^2 cross section and what temperature rise was experienced.View attachment 27014
View attachment 27015
Busbar... How about just use cable.. This green stuff was only the ground cables at a place I was helping re-commission. We pulled out all the DC cable and scrapped it. $64,000 of scrap. !!! I was shocked.
The busbar was 12 inches wide and 3/8" thick and it was ALL doubled-up to be 3/4" thick. The batteries where each 4 feet wide and 8 feet long and filled a room the size of a basket ball court.
The battery chargers... nine of them. 800A @ 58V
View attachment 27018
The conversation has recently turned to the current capacity of bus bars by the area of the cross section. It sounds like you have expertise in the subject.Sorry but it's unclear to me how to arrive at those numbers because the busbars had the battery chargers running to them at various locations and then the loads were pulled off in a distributed manner all over the busbars and routed to a dozen DC distribution panels. It wasn't a simple clean 'batteries here load there' type system. It was a massive phone switching system facility (World Com).
Are you asking about short circuit aspects?
Or a steady-state operating thermal limit?
Do you have a voltage drop you're willing to live with at a maximum normal discharge rate?
What exactly are you seeking?
An easy, though usually over sized method, for determining minimum bus bar size.
-Consult the 90C insulation ampacity table for standard cable (AWG or metric) for your expected max continuous current.
-Convert the AWG to cross sectional area.
Take the cross sectional area, and find an equivalent bus bar. Its typically okay do go down 1AWG size, as bus bars will be rectangular usually, and thus have more surface area than a cable.
The dimensions shown are 2mm x 20mm (40 mm²)
I can't find a good metric ampacity table so this one will have to do
The smallest busbar on that list 1/8" x 1/2" is also roughly 40 mm²
and is rated for only 150A DC
For reference 40 mm² = 79,000 circular mils = a cross section in between 2AWG and 1AWG
Wouldn't the upper limit of 90*C rated wire mean the copper would be close to 90*C? And wouldn't temps close to the boiling point of water be quite undesirable right at the battery terminals?
This raises an important point, what is acceptable/allowable depends on the context. And it seems like 'distribution' busbars (my own term, there is probably a better or more standardized term), and 'cell interconnection' type busbars are very different contexts.Your right, If you are attaching directly to a battery, I would derate by 1-2 AWG sizes larger. I chose 90C, as the bus bars typically cool significantly better. For more conservative estimates, you can just go with the 70C tables.
Seems they can sustain 400A (as seller said)
Could you explain briefly how this is derived?The bus bar would only be 90C if the ambient was 45C or so.
Essentially for a given wire, there is a certain Delta T otherwise known as temperature rise required to dissipate the heat generated at that wires rated current. the current limit is specified based on an expected ambient temperature and the insulation rating. For example most marine wire is rated for an ambient of approximately 30c and with 90 C insulation. that results in a 60 C temperature rise at rated current. If that wire passes through an engine compartment, it must be derated to .85 of its normal current rating. It is assumed in a marine application the engine compartment will not exceed 50C. Since only 40C rise is available, 40/50~80% available current limit.Could you explain briefly how this is derived
Perhaps an analogy would be a water pipe, heating of the wire could be the increased tension on the pipe due to pressure... If you try to push more water in the pipe, the friction will tend to increase pressure... Same for wanting to increase the current, the quantity of electron you want to pass through the wire... too much and instead of flowing through the wire they hit themselves increasing the température.This raises an important point, what is acceptable/allowable depends on the context. And it seems like 'distribution' busbars (my own term, there is probably a better or more standardized term), and 'cell interconnection' type busbars are very different contexts.
If you go back a page Post #276-277 the conversation began with a discussion of these cell Busbars:
Could you explain briefly how this is derived?
I understand how to read an ampacity chart and ambient and insulation temperature rating.
But I am completely ignorant of the math that goes into determining how much a conductor's temperature will rise for a given current.