Why are you assuming imbalance is the issue?
Have you hooked up a surge meter to see how much surge current the grid supplies when starting that miter saw?
My guess is that that miter saw needs everything the inverter can supply to get started and if any other loads are being powered by the same leg, it doesn’t have the surge capacity to get that miter saw started.
If I’m correct, this issue has nothing to do with ‘imbalance’.
Because we'd find a trip error of:
'F26 - BusUnbalance_Fault - Too much load on one leg (L1 or L2) Vs. the other leg or DC loads on the AC output when off-grid. Grounded PV +/- wire can cause F20, F23, or F26. '
And so if you turn on some other loads on the other leg then the trip goes away, or is way less likely to occur.
Based on my research it has something to do with the inverter control circuit's ability to cope with a sudden imbalance of impedance (and voltage-drop) between the output phases.
And a consumer added-on auto-transformer proves in other cases to help the legs share some current (balance the impedance somewhat) from the other adjacent leg (by having the extra resistors bridged across and a neutral connection in the middle).
The LF inverters probably aren't as susceptible to imbalance issues since they essentially have the same thing like an auto-transformer (or isolation transformer with the center tap already in them to help balance out the legs.
So I don't really know if this phenomena is specific to SolArk all-in-one split-phase HF, or other brands as well, or not likely to occur on LF all-in-one split-phase or anything.
I was just emphasizing that I prefer the paired 120v inverter approach, joined to become split-phase, better (in my experience), since I have seen them run under all sorts of severely imbalanced loads, and know they don't care how the loads are being placed on them, because each inverter has its own inverter controller board running its own set of switches.
I haven't even got my own LV6548s running online yet, just been working with neighbors with 6500EX mostly, and one who has six LV6548, one guy with the two Sunny Islands 6048-US on a solar trailer, etc, and I do like how this topology operates.
That's really not what this thread is about, so sorry if I took it off into left field, I had mainly replied to Zwy explaining why I love the separate inverter per phase. Not saying this new MPP Solar 10kw would have any sort of issue related to imbalance, guess someone can test it more as things progress.