The direction of the CTs can be flipped if you also swap the wires. Depending on space and how the wires leave the CT, it can sometimes be easier to have it turned around and then connect the wires the direction that results in the correct readings. If the wiring and CT direction are opposite to each other, then import and export power readings will be reversed. Think of it like a 3 way light switch setup. If both are the same way, it's okay (the light is on), if only one is flipped, the reading will be backwards (the light is off).
The bigger issue I see with that install is the lack of a decent strain relief or at least a rubber grommet on the wires. And I would use a weather sealed type as well. That raw drilled hole is going to wear through those wires and short them to ground.
The bigger issue I see with that install is the lack of a decent strain relief or at least a rubber grommet on the wires. And I would use a weather sealed type as well. That raw drilled hole is going to wear through those wires and short them to ground.