Can I run a grounding wire 150ft from PV array to inverters?

The most important thing is to have PV frame grounded to house ground stake directly and NOT to have PV frame directly connected to a separate ground stake with some distance from house ground stake. That is almost guaranteed to have thousands of volts be applied to your charge controller input from a nearby lightning strike.

A good solution is to run a ground wire from panels frame to common house ground stake and place ground stakes near the panels with a spark gap lightning suppressor in series with panel local ground stakes.

The ground wire from PV panel frame to house ground should be run along outside of house and not be brought inside of structure to avoid any flash over to items within house.

The common ground wire to single main breaker box ground stake keeps potential difference of house ground and incoming PV power lines low so a nearby lightning strike with thousands of volts difference from remote ground stakes does not damage your equipment. You should still have good surge suppressors on charge controller inputs to house ground stake connection. Most charge controller have these but good to supplement with additional external suppressors.

If by chance, lightning hits panel framing, the spark gap lightning suppressor to PV local ground stakes will bridge taking most of the direct lightning hit directly to PV local ground rods.

If you live in a lightning prone location another option is to place lightning rods, above and a few feet away, around PV array, with lightning rods connected to local ground stakes with no connection from lightning rod ground to panel framing which goes to house ground stake. This is similar to what NASA does around a launch pad to protect a rocket. For this need to consider placement of lightning rods to avoid shading on PV panels. Most of the time, lightning rods bleed static charge build up preventing a direct lightning strike. They have pointed tips to enhance corona discharge of charge build up.

Because any ground wire may get hit with high impulse current during a lightning strike it is best not to place ground wire bundled in parallel with PV power lines in a common conduit. The high ground wire impulse current can induction couple a high voltage impulse on the parallel wires of the PV charge controller inputs.
 
Last edited:
But… aside from your inverter putting ac on your PV circuit (which couldnt even happen if your mppt and inverter weren’t the same box), why would the PV array need to be electrically grounded? Im still missing something.
DC shock Hazzards can also be deadly.
Ground fault protection is also required for the PV DC circuits.
 
DC shock Hazzards can also be deadly.
Ground fault protection is also required for the PV DC circuits.
So, i understand the normal DC hazards but I was not getting how tieing the PV frame to the house (aka AC electrical system) ground was making anything safer for the human because it didn't improve anything about you creating a 'path back to source' with your body.. On the DC side you'd have to have body parts touching something on both 'poles' of the DC circuit to get the juice flowing, in which case the ground conductor changes nothing because it's not tied to either one except in case of ground fault. So it wouldn't seem to reduce the DC hazard any in the absence of a ground fault.. But if one side HAS a ground fault, it increases the likelihood that you end up touching both sides of the circuit at once, because now the entire sea of panels you're standing in is one side of the circuit! The actual grounding rod at the house won't pull the DC voltage down because the dirt has no path back to the other side of the DC circuit, and if it did because BOTH sides of the DC circuit have a ground fault out to the panel framing, the panels would short locally through the racking and the ground conductor into the house would do nothing anyway.

On the AC side you would only have AC out there if your house equipment was putting it there, and having a copper conductor back to house ground was just giving your pv panelling a BETTER path back to the AC source, than if you touched the live AC and a pv panel frame and that copper conductor wasn't there! X amount of AC voltage pushing against my body plus 150' of dirt resistance back to house ground rod back up into the panel to the NG bond, across the neutral back to source, is a lot less likely to give me the wiggles than my body plus 150' of beautiful perfect copper directly back to the source. So it would seem to me to be making the AC hazard worse.

I guess the way it could help is if it put the PV panel framing/racking at the SAME potential as the live wire you're touching. But that would require a 'ground fault', ie some low resistance path between the conductor carrying the AC, and the framing/racking. If there IS no ground fault, but you end up touching the AC anyway, and the PV panel frame, then the two things are at very different potential and you get the wiggles.

It just seems like ground faults are not the only type of fault, and this is making a bunch of other types of faults (including human error) more dangerous and only really helping in the event of lightning. I must have some major fundamental blind spot for all these downsides to somehow be wrong, or for there to be such a big upside somewhere else that it outweighs all these downsides. It's unnerving. I hope to get to the bottom of it soon. :oops:
 
Last edited:
So, i understand the normal DC hazards but I was not getting how tieing the PV frame to the house (aka AC electrical system) ground was making anything safer for the human because it didn't improve anything about you creating a 'path back to source' with your body.. On the DC side you'd have to have body parts touching something on both 'poles' of the DC circuit to get the juice flowing, in which case the ground conductor changes nothing because it's not tied to either one except in case of ground fault. So it wouldn't seem to reduce the DC hazard any in the absence of a ground fault.. But if one side HAS a ground fault, it increases the likelihood that you end up touching both sides of the circuit at once, because now the entire sea of panels you're standing in is one side of the circuit! The actual grounding rod at the house won't pull the DC voltage down because the dirt has no path back to the other side of the DC circuit, and if it did because BOTH sides of the DC circuit have a ground fault out to the panel framing, the panels would short locally through the racking and the ground conductor into the house would do nothing anyway.

On the AC side you would only have AC out there if your house equipment was putting it there, and having a copper conductor back to house ground was just giving your pv panelling a BETTER path back to the AC source, than if you touched the live AC and a pv panel frame and that copper conductor wasn't there! X amount of AC voltage pushing against my body plus 150' of dirt resistance back to house ground rod back up into the panel to the NG bond, across the neutral back to source, is a lot less likely to give me the wiggles than my body plus 150' of beautiful perfect copper directly back to the source. So it would seem to me to be making the AC hazard worse.

I guess the way it could help is if it put the PV panel framing/racking at the SAME potential as the live wire you're touching. But that would require a 'ground fault', ie some low resistance path between the conductor carrying the AC, and the framing/racking. If there IS no ground fault, but you end up touching the AC anyway, and the PV panel frame, then the two things are at very different potential and you get the wiggles.

It just seems like ground faults are not the only type of fault, and this is making a bunch of other types of faults (including human error) more dangerous and only really helping in the event of lightning. I must have some major fundamental blind spot for all these downsides to somehow be wrong, or for there to be such a big upside somewhere else that it outweighs all these downsides. It's unnerving. I hope to get to the bottom of it soon. :oops:
If you had a DC ground fault. The ground fault protection can't detect it and shut it down, if there is no ground.
Sorry, that's all that I have.
 
And then the inverter is grounded to the service ground bar, hopefully.
I'm looking at my inverters diagram since it hasn't arrived yet (it's the EG4 6500EX) and I don't see any ground connection for the PV inputs. It's on page 19 of this manual. You can also see at this timestamp of Will's video that there is only the positive and negative PV connections, but no ground.

I have ran my ground through my attic with my positive and negative PV wires, going from my arrays to my inverters.
 
I'm looking at my inverters diagram since it hasn't arrived yet (it's the EG4 6500EX) and I don't see any ground connection for the PV inputs. It's on page 19 of this manual. You can also see at this timestamp of Will's video that there is only the positive and negative PV connections, but no ground.

I have ran my ground through my attic with my positive and negative PV wires, going from my arrays to my inverters.
It's the same ground for everything. There's not a dedicated PV ground terminal. It just needs to be connected to the rest of the grounding system.
 
The only DC ground fault detection that I am aware of does not measure imbalance like AC detection. It looks for actual voltage on the ground.
Nope , for example here’s Morningstar DC protection, it’s clearly stated it uses current imbalance
 

Attachments

  • 6C8A03A7-8741-4F9F-8325-27931D062501.jpeg
    6C8A03A7-8741-4F9F-8325-27931D062501.jpeg
    276.7 KB · Views: 9
Nope , for example here’s Morningstar DC protection, it’s clearly stated it uses current imbalance
I see.
I didn't think that anyone was using that type anymore. Because it can't detect a low enough leakage.
As pointed out in the write up you posted above.
But I guess some are still selling it.
Thanks
 
It's the same ground for everything. There's not a dedicated PV ground terminal. It just needs to be connected to the rest of the grounding system.
I just spoke with Signature Solar who is the distributor of my inverter and they said under no circumstances should I connect a grounding wire from my solar arrays to my inverter. They said there isn't even a place to connect it because the only two ground lugs are for the AC input and output.
 
I just spoke with Signature Solar who is the distributor of my inverter and they said under no circumstances should I connect a grounding wire from my solar arrays to my inverter. They said there isn't even a place to connect it because the only two ground lugs are for the AC input and output.
That's what I said above.

It's the same ground for everything. There's not a dedicated PV ground terminal. It just needs to be connected to the rest of the grounding system.
 
Again gentlemen the general is independant grounds are not interconnected. One ground point per system.
Code requires minimum TWO ground rods at service connection point, and additional are approved. As long as all are connected together.

Panel emf dissipation grounds doesn’t need to be tied to the main panel grounding circuits.
 
It's the same ground for everything. There's not a dedicated PV ground terminal. It just needs to be connected to the rest of the grounding system.
Understood. So I can run this grounding wire from my panels and clamp it the the grounding wire coming off my service panel that goes into the earth ground rod?
 