By the way, another question on this same topic:
Solis has been selling a 240VAC inverter with a companion Autotransformer in the US for years:
https://www.renvu.com/Solis-5kW-Sin...rage-Hybrid-Inverter-with-SunSpec-Transmitter
There is a manual transfer switch integrated into their Autotransformer to enable the inverter to be bypassed powering critical loads so that the inverter can be serviced without interrupting power to critical loads, but the Autotransformer itself seems to always be wired to L1 and L2 under normal operation, exactly as we’ve been concerned crème’s about here.
There is no neutral connection of any kind on the inverter itself while the Autotransformer has both a Neutral in from grid as well as a neutral out to critical loads.
And as far as I’ve been able to understand, there are no automatic transfer switches within the Autotransformer - just the manual switch to bypass the inverter.
So either Critical Loads is being served with an independent Critical Loads Neutral formed by bonding center tap of the Autotransformer to ground always (meaning all critical loads together appear to the grid as a single combined 240V load) or this set-up suffers from the ‘two transformer coils both trying to balance load’ problem we are discussing here.
I’m in contact with their US support staff who have one of these installed on their home and hey have agreed to perform some simple tests using a multimeter for me.
So my question is, can anyone think of a simple test to:
1/ determine whether the critical loads Neutral is shorted to Mains Neutral or not? (Ideally without cutting AC power)
2/ if the Autotransformer is always connected to L1, L2 and N (as I suspect), is there an easy test to determine whether there are any currents flowing of the sort we are concerned about (full-house balance currents as well as any currebts flowing through neutral from Autotransformer to transformer on utility pole)?
Solis has been selling a 240VAC inverter with a companion Autotransformer in the US for years:
https://www.renvu.com/Solis-5kW-Sin...rage-Hybrid-Inverter-with-SunSpec-Transmitter
Solis External Autotransformer
DetailsSolis External AutotransformerSolis External Autotransformer Solis-ATR-6K autotransformer is designed to be used with the Solis energy storage inverter RHI-1P(5-10)K-HVES-5G. The ATR can support 120VAC backup loads with up to 7kW of output power. An integrated bypass switch ensures a high...
www.renvu.com
There is a manual transfer switch integrated into their Autotransformer to enable the inverter to be bypassed powering critical loads so that the inverter can be serviced without interrupting power to critical loads, but the Autotransformer itself seems to always be wired to L1 and L2 under normal operation, exactly as we’ve been concerned crème’s about here.
There is no neutral connection of any kind on the inverter itself while the Autotransformer has both a Neutral in from grid as well as a neutral out to critical loads.
And as far as I’ve been able to understand, there are no automatic transfer switches within the Autotransformer - just the manual switch to bypass the inverter.
So either Critical Loads is being served with an independent Critical Loads Neutral formed by bonding center tap of the Autotransformer to ground always (meaning all critical loads together appear to the grid as a single combined 240V load) or this set-up suffers from the ‘two transformer coils both trying to balance load’ problem we are discussing here.
I’m in contact with their US support staff who have one of these installed on their home and hey have agreed to perform some simple tests using a multimeter for me.
So my question is, can anyone think of a simple test to:
1/ determine whether the critical loads Neutral is shorted to Mains Neutral or not? (Ideally without cutting AC power)
2/ if the Autotransformer is always connected to L1, L2 and N (as I suspect), is there an easy test to determine whether there are any currents flowing of the sort we are concerned about (full-house balance currents as well as any currebts flowing through neutral from Autotransformer to transformer on utility pole)?
Last edited: