Part #2: IQ8+ AC Coupled to XW Pro 6848:
Schneider XW Pro 6848: Firmware 2.04.00bn29
IQ Gateway: Software 7.3.120
IQ8+: (4 total) Firmware 521-00005-r05-v02.48.01
Grid Profile: IEEE 1547-2015 (Colorado default)
PV Amp Meter (CT): PZEM-022 AC Current Voltage Amperage Power Energy Panel (AC Volt, AC Amp, Frequency (Hz), PF)
Off-Grid Test:
4 x IQ8+'s take about 5 min 15 sec for the micro-inverters to lock on to the micro-grid
4 x IQ8+'s produce about 1.2 kW = 4 x 299W
SOC 100%: XW Pro raises frequency by 1 Hz to 61 Hz, IQ8+'s shut off within 1-2 seconds.
XW Pro frequency back to 60 Hz, IQ8+'s stay off
SOC drops to about 99%: IQ8+ inverters lock-on again after 5 min and 20 sec.
works with or without IQ gateway connected
On-Grid ... Grid-Fault/Off-Grid ... On-Grid Test:
Grid Voltage: 249V
4 x IQ8+'s take about 5 min 15 sec for the micro-inverters to lock on to the grid
about 1.2 kW PV flows into the grid and into the batteries
On Grid-Fault: IQ gateway reboots, micro-inverters switch off
Inverter Voltage: 240V, about 9v less than grid, IQ8's log change in voltage
After about 4.5 minutes, the IQ8's lock on to the micro-grid and produce 1.2 kW
Grid-Back: IQ8's switch off, lock on after 4.5 sec and produce 1.2 kW
I would say that is a fairly successful test. So far, it is doing nothing unexpected and performing better than I was expecting.
I am still concerned about pumping 8000-9000 watts into the inverter if I ever have a power failure in full sun and the batteries are fully charged. I have some ideas on how to rewire my system to allow the following:
1. Grid power is on (use 240 Volts AC from AC1 Grid In). The PV contactor should always be energized. Relays controlling each individual string would also always be on. Excess production will flow back to the grid.
2. Grid power is off (use 240 Volts AC from AC1 Grid In). The PV contactor will only be energized when SOC or battery drops below a certain point. This should be possible by setting up the Auxiliary relay control signal.
3. Grid power is off (use 240 Volts AC from AC1 Grid In). Only turn on selected PV strings. This might need some level of management. It might be different between winter and summer.
4. Power the Envoy board from the AC Load Out (so it does not reboot every time the PV contactor disconnects).
There is still a potential issue if the inverter disconnects for a reason other than a full power failure or during the time when power has come back on, but the inverter has not yet reconnected to the grid. It appears the Schneider can still knock the PV inverters off line if it needs to. I have noticed that after a grid failure, the PV inverters do not just suddenly come back on at 100%. They ramp up slowly which should give the Schneider time to do its "Frequency Pulse" thing. I have also seen this same frequency pulse when I have been testing with the battery above the SOC where you would expect the Schneider to dump its excess power into the battery.
So from what I am seeing, a couple things are true.
1. If your system SOC is above the level where AC coupled charging should occur: You need to have enough Inverter and Battery Capacity to handle the excess output of the PV inverters and store it in the batteries long enough for the Schneider to send its "Pulse of Death" to the PV inverters to get them to shut down. Without a PV disconnect mechanism, I believe this will happen over and over every 5 minutes.
2. If your system SOC is below the level where AC coupled charging should occur: You need to have enough Inverter and Battery Capacity to handle the excess output of the PV inverters and store it in the batteries long enough for the Schneider to ramp down the the PV inverters (through frequency shifting) to a level that is in line with usage and battery charging requirements.
In other words, when AC coupling you want to maximize the amount of battery and inverter power, while also minimizing the amount of PV (or at least getting it down to a manageable level).
For me at least (knock on word) I am hoping that true grid down situations will be fairly rare and will not be extended. Maybe further testing will show that the Schneider can manage all of this out of the box without any additional addons. We shall see.
FYI, before I fine tuned my charging parameters, I had the charging set to 140 amps per inverter. I think this is the default. So with two inverters and three batteries, I was pumping 14,000 watts into the batteries. They can handle up to 100 amps each, so this was an acceptable load. Anyway when the chargers turned on, I was sure my system was about ready to "Blow". There was an enormously loud 60 cycle hum. It turns out it was just wire tray covers resonating and nothing was actually wrong. Just because your system can handle a load doesn't mean you really want to put that much load on it. It seems far happier charging at 30 amps per inverter / 20 amps per battery.