4 gauge wire for panels to SCC is crazy.I think I have a better idea of what I need now. The only thing I forgot to add to the cart is the 4 gauge wire to go from the junction of all the panels to the SCC.
To break it all down:
1. 8awg wire for between the 4 to 1 branch connectors and junction.
2. Power distribution block (need to add one more).
3. 1500W inverter.
4. Epever 40A controller.
5. Crimp connectors for various 12V needs.
6. 4 to 1 branch connectors.
7. Inline fuses for between the panels and branch connectors. (Still need to find 7A fuses)
8. 2 to 1 branch connectors (need to remove)
9. USB socket.
10. Inverter cables.
11. Circuit breaker for between battery and inverter.
12. Bus bars for 12V power distribution. Thinking 10g wire to the bus bar from the fuse block, then 14g wire to the different light circuits.
4 AWG???? Lucky that you forgot to buy them.I think I have a better idea of what I need now. The only thing I forgot to add to the cart is the 4 gauge wire to go from the junction of all the panels to the SCC.
To break it all down:
1. 8awg wire for between the 4 to 1 branch connectors and junction.
2. Power distribution block (need to add one more).
3. 1500W inverter.
4. Epever 40A controller.
5. Crimp connectors for various 12V needs.
6. 4 to 1 branch connectors.
7. Inline fuses for between the panels and branch connectors. (Still need to find 7A fuses)
8. 2 to 1 branch connectors (need to remove)
9. USB socket.
10. Inverter cables.
11. Circuit breaker for between battery and inverter.
12. Bus bars for 12V power distribution. Thinking 10g wire to the bus bar from the fuse block, then 14g wire to the different light circuits.
Good catch, I checked and 6 gauge is the biggest that can fit.Make sure the 4 gauge wire fits in your solar charge controller. My Victron spec sheet says 6 gauge max. It was pretty close with 6 gauge. If your controller has studs for ring terminals then nevermind.
4 AWG???? Lucky that you forgot to buy them.
2S4P 100 watt panels
37Vmp
21.6A Imp
15 feet one way on a camper?
Only needs 10 AWG for about 2% voltage drop.
You can change the inputs on this calculator.
Voltage Drop Calculator
This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current.www.calculator.net
12V battery?Except I've decided on 12V... Forgot to mention. Stop at 46.8A, is 4-6 gauge still over kill?
And what watts is them panels??The specs of the panels I want to buy... they will be wired in paralell
Isc: 5.86A X 8 = 46.8A
So im thinking 6-8 gauge between the panels and SCC, and the same from the SCC to battery
800w panels even at 14V needs 57A.2s4p was only a consideration when I was confused about my options for an SCC. I thought I would need more controller that I would actually need. So I thought for a sec about going with a 24V system.
But that's cleared up now. And I'm back to my original 12V plan. 800W panels, and a 40A controller.
Ahhh, I see. I thought you would only series connect panels if you were running a 24V+ system...800w panels even at 14V needs 57A.
40A x 14V is only 560 watts out of your 800 so you are over panelled
Wiring 2S4P or 8P has not much to do with battery voltage.
What brand and model is your SCC?2s4p was only a consideration when I was confused about my options for an SCC. I thought I would need more controller that I would actually need. So I thought for a sec about going with a 24V system.
But that's cleared up now. And I'm back to my original 12V plan. 800W panels, and a 40A controller.
Reason I'm having trouble deciding is because 8 panels will make a max of 180.8V ... And the 80A controller can handle 200V max.
Diagram is 2S4P so only 45Voc so plenty of room for really cold temps even on a 100V max input SCC.180.8V would be too much for a 200V controller.
Panel spec are given at 25 degrees C, and if you visit a freezing area the Voc could increase 15%
Look up temperature coefficient on data sheet (or use a conservative assumption) and calculate adjusted Voc for historical record cold temperature.
(your most recent diagram doesn't look like many panels in series, but double-check whatever you plan to build. And check actual voltage with DMM before connecting to SCC.)
Nowhere on your diagram does it say 12V battery or inverter.