High Frequency vs. Low Frequency Inverter - Does it matter??

So another user reported their ACTUAL 5kva Victron Quattro idle consumption of 55w
That is a 120v 4k LF inverter with toroidal transformer
@HighTechLab mentioned a high sigineer idle consumption but I contend with the following:
To achieve the equivalent 12k inverter capacity, one would need 3 of the 5kva Quattro (ignoring the 3 phase instead of split phase issue).

3x55w=165w
What am I missing? That’s also excluding MPPT which is separate.

To be clear. I’m not contending that the sigineer/Growatt are nearly as efficient, robust, or reliable as the Victron.
But if the biggest qualm is idle consumption.
And 12k and LF, it sounds like it’s part of the territory
Multiplus-2 5kva: 15w measured and LF

If you can handle the higher idle, by all means go for it. But it wasn’t good for our situation on my parents property. Just my experience with Sigineer, and there are videos of it on my HighTechLab YT channel
 
Not sure what my 30 yr old 220 well pump hp is but it starts it every time as well as my 24k mini split.
Well pump HP depends on well depth and GPM desired. Roughly a 1/2 hp pump will do a 200' deep well, 3/4 hp up to 300', 1 hp 400' and 1.5 hp for a 520' deep well. (Data for 7.5 GPM)

PumpW.png
 
Multiplus-2 5kva: 15w measured and LF

If you can handle the higher idle, by all means go for it. But it wasn’t good for our situation on my parents property. Just my experience with Sigineer, and there are videos of it on my HighTechLab YT channel
Yeah I messaged your sales page after watching some videos a month or two back. Always a plethora of info!
 
It may be that the industry is trying to move to HF inverters (or some hybrid thereof), but I think OP has these considerations that IMHO would tend to favor LF inverters:

- heavy house loads, *shop* loads
- HF inverter threads abound with (warranty, support, etc.) issues

I'd utilize a tier-1 LF inverter (although a hybrid might fit), and you'd probably get beyond 5 years or more with the core inverter. With the HF lines, I'm not so sure you'd get to the same number of years, regardless of HF "long-warranty" claims (which then have to have good support behind the claim).

Finally, any RE system, and especially those running a shop or possibly having spot/peak loads (weird HVAC units, in combination with other house loads), should consider a backup generator as part of the system. Not only will this backup solar panel output, it could carry peak or heavy spot loads, if the inverter is capable of gen auto-start.

I don't see (yet) when HF inverters match up to LF inverters in terms of performance/warranty/support, and one could count on them to run your house for upwards of 5 years or more. For the record, I am still on LF inverters (magnum), and my HF projects are small potatoes effort at this time (hand truck solar generator effort), but that's because of warranty & such (as in, some of these HF units have almost no warranty, which I equate to "quality of build").

If I were to try and run my house/loads on HF, I think I'd need at least 2 inverters, and possibly more as spares, to overcome such warranty/quality issues ... I do hope we see a time when *many* folks say "I've run my house on HF for 5 years now, the warranty has expired at 5 years, and things are still cooking", or something similar.

Hope this helps ...
 
Everything Ive read from specs to warranty horror stories to just plan failures I doubt I will ever go HF. Unless they quit making LF inverters. To much hassle/risk for real world loads. I don't want to have to run around installing soft start units and other stuff when I can just enjoy it all just working.

Its just way to handy having all of that surge on hand when needed.
 
You gotta think that most of the population is also grid tied, or at the very least grid assist. This is why I have 1x SolArk 12k (a 9kw HF inverter), and have no problem running my whole house, including a 5 ton AC, because the grid is there for my surge. And since the inverter is just pumping kWh's out and not getting the harsh surge, I expect it to last ATLEAST 5 years, and hopefully 10 or more.

The amount of people who are completely off-grid and need 50kW of LF surge capability are very few and far between. This is why companies are getting away from LF. Even newer appliances are needing less inrush current as the years go by, like inverter type mini-split air conditioners.
 
I’d contend that more people are going off grid now than ever before and LF is becoming an afterthought at a terrible time
 
Even if everyone on those forum went off-grid, it's still probably .001% of the population that's is doing Solar.
Imagine how many less "my such and such" won't turn on or start even though it should use less watts than what my inverter says it can do threads would never of happened :)
 
Imagine how many less "my such and such" won't turn on or start even though it should use less watts than what my inverter says it can do threads would never of happened :)
Imagine how many "my 800lbs inverter fell off the wall because I out 1x 1/4" Wood Screws in the wall"

Or "why do I keep running out of battery in the middle of the night?" "Because your inverter has way too much idle draw".

We can go round and round about it. At the end of the day, I agree that the LF inverter has its place, and is necessary, but its not for everybody, and not even for the majority of people.

I personally would rather have 2x HF inverters that can start my offgrid AC and Well pump, and maybe even add in a SoftStart to make my AC and equipment last longer, rather than have just 1x LF inverter that I have to rely on to survive.
 
The Genetry Solar 12 kW idles at about 30 watts unloaded. There's a generally negative opinion about them, and in dealing with them I'd say it's earned. But not for the inverter. The inverter is 100% tank. Super solid machine and way under priced.
 
Imagine how many "my 800lbs inverter fell off the wall because I out 1x 1/4" Wood Screws in the wall"

Or "why do I keep running out of battery in the middle of the night?" "Because your inverter has way too much idle draw".

We can go round and round about it. At the end of the day, I agree that the LF inverter has its place, and is necessary, but its not for everybody, and not even for the majority of people.

I personally would rather have 2x HF inverters that can start my offgrid AC and Well pump, and maybe even add in a SoftStart to make my AC and equipment last longer, rather than have just 1x LF inverter that I have to rely on to survive.
I agree with all but the last line.

I'd rather be able to afford FOUR or more LF inverters to the two hf inverters (sol-ark's pricing). I'd buy two max giving 12k with 36kw surge vs a single sol-ark 12k and have money left over to buy batteries to make up for any extra draw or have 8 LF inverters for the same money with 32kw RAW power and 96 KW surge :)

Two each their own though. That's the beauty of the world at least right now we can all go with what we want and its all good.
 
I personally would rather have 2x HF inverters that can start my offgrid AC and Well pump, and maybe even add in a SoftStart to make my AC and equipment last longer, rather than have just 1x LF inverter that I have to rely on to survive.
There is certainly merit in having a backup, no argument there.

The alternative is a very simple robust easy to fix LF inverter with enough spares to be able to repair anything that might fail.
These days almost everything is deliberately designed to be obsolescent, cheap, and unrepairable.

While having wifi, data logging, a graphics screen, sound effects, and internet connection may be nice, none of that is needed to turn dc into some usable ac.
These days when all the fancy technology stops working, its usually unrepairable, even by a professional.
 
You gotta think that most of the population is also grid tied, or at the very least grid assist. This is why I have 1x SolArk 12k (a 9kw HF inverter), and have no problem running my whole house, including a 5 ton AC, because the grid is there for my surge. And since the inverter is just pumping kWh's out and not getting the harsh surge, I expect it to last ATLEAST 5 years, and hopefully 10 or more.

The amount of people who are completely off-grid and need 50kW of LF surge capability are very few and far between. This is why companies are getting away from LF. Even newer appliances are needing less inrush current as the years go by, like inverter type mini-split air conditioners.
I think a lot of those folks running their big loads with grid available will prob be surprised if there's a grid outage and their inverters can no longer deliver what they thought they could. Because surely they also spent that money to also have the same experience when grid is offline? The grid goes out and no air conditioning? I guess as long as grid stays up all is good. But for some that understand the tech, they want the performance to power loads without relying on the availability of the grid. Grid is nice to have but full performance can be obtained without it.
 
I think a lot of those folks running their big loads with grid available will prob be surprised if there's a grid outage and their inverters can no longer deliver what they thought they could.
Oh it goes way beyond that.
Wait until gasoline costs fifteen dollars a gallon, and people will be whining about not being able to aford to run their 800 horsepower sports truck.
 
So another user reported their ACTUAL 5kva Victron Quattro idle consumption of 55w
That is a 120v 4k LF inverter with toroidal transformer
@HighTechLab mentioned a high sigineer idle consumption but I contend with the following:
To achieve the equivalent 12k inverter capacity, one would need 3 of the 5kva Quattro (ignoring the 3 phase instead of split phase issue).

3x55w=165w
What am I missing? That’s also excluding MPPT which is separate.

To be clear. I’m not contending that the sigineer/Growatt are nearly as efficient, robust, or reliable as the Victron.
But if the biggest qualm is idle consumption.
And 12k and LF, it sounds like it’s part of the territory
The newest Quattro II 5kVA (currently only in 240V) has a listed idle of 18W. I'm assuming the larger Quattro IIs to come will also have a significantly lower idle versus the Quattro I's.

Screenshot_20230906_190203_Samsung Notes.jpg
 
I think a lot of those folks running their big loads with grid available will prob be surprised if there's a grid outage and their inverters can no longer deliver what they thought they could. Because surely they also spent that money to also have the same experience when grid is offline? The grid goes out and no air conditioning? I guess as long as grid stays up all is good. But for some that understand the tech, they want the performance to power loads without relying on the availability of the grid. Grid is nice to have but full performance can be obtained without it.
I won't be surprised. My SolArk 12k purposely doesn't power my main panel (where the AC or dryer are at), it only powers the sub panel in the garage, with the lights, outlets, kitchen, and garage etc, and then backfeeds the main panel. In the event of a power outage, I will have no A/C.

Knowing that, I also havent had a power outage that I have noticed in the last 10 years. I've only had solar for the last 3.
 
The Genetry Solar 12 kW idles at about 30 watts unloaded. There's a generally negative opinion about them, and in dealing with them I'd say it's earned. But not for the inverter. The inverter is 100% tank. Super solid machine and way under priced.
Interesting - I looked them up, Genetrysolar.com they spec the 12kW LF at 48W idle consumption - impressive for a 12k LF. I notice they offer the 12k in various voltage (customer can choose) 24, 36, 48 60 (TBD) - I don't think I can even imagine a 12k running 24v - likely they derate the output to hold the amperage to acceptable levels. Interesting to see 36-volt. They say US assembly.

At $2,999USD for the 12K - that is pretty solid value. List at 111 pounds, 125 shipping weight (ok must be LF)
Which model are you running?
Do you pair up two inverters or run a single?
How long have you been operating it - what loads do you handle with it?
 
Last edited:
Interesting - I looked them up, Genetrysolar.com they spec the 12kW LF at 48W idle consumption - impressive for a 12k LF. I notice they offer the 12k in various voltage (customer can choose) 24, 36, 48 60 (TBD) - I don't think I can even imagine a 12k running 24v - likely they derate the output to hold the amperage to acceptable levels. Interesting to see 36-volt. They say US assembly.

At $2,999USD for the 12K - that is pretty solid value. List at 111 pounds, 125 shipping weight (ok must be LF)
Which model are you running?
Do you pair up two inverters or run a single?
How long have you been operating it - what loads do you handle with it?
I have two 12 kW installed on separate systems in the same building. 48 volts. These were desired by the customer and I installed them. They are NOT UL listed, so that may be a non-starter for some people. I have over 500 kWh through one of them so far with over 1000 hours of uptime. They start a 1 HP well pump no problem. They start a 4 ton A/C no problem. I have no complaints about the hardware.

But the business side is bad. It's just a two man operation and they are struggling to meet demand. It took 4 months to get these inverters. I'm still waiting on a 6 kW.
 
Hopefully we will get away from single phase AC motors as much as possible, but it would be sad to see LF inverters less available.

I replaced a 1/2 HP Goulds jet pump (1350VA before inverter losses) with a 12V 260W RV pump and it does the same job in the same time frame, about 45 seconds to pull 2.5 gallons from a shallow sand point and into the pressure tank. 6X less watt hours not to mention no massive startup spike. I had a separate 3000W HF inverter on standby just for that pump, now it's a backup inverter.

I cool the house with a pair of Midea U 8000 BTU window units that are inverted DC, have no startup spike and really sip power. They are incredible dehumidifiers on dry mode. Paid $150ea on FB market.

Window fans (100W) and inline fans (200W) can now be replaced with $65 inverted or direct DC inline fans that pull 65 watts max. Same goes for washing machines, fridges, dehumidifiers, vacuums, ceiling fans, power tools and furnace blowers. This really is some game changing tech.

95% of the time I run the house on a 120V 3500W HF inverter with 6 watt standby power...until the GF comes over then I might fire up the LF ?
 
Last edited:
I have two 12 kW installed on separate systems in the same building. 48 volts. These were desired by the customer and I installed them. They are NOT UL listed, so that may be a non-starter for some people. I have over 500 kWh through one of them so far with over 1000 hours of uptime. They start a 1 HP well pump no problem. They start a 4 ton A/C no problem. I have no complaints about the hardware.

But the business side is bad. It's just a two man operation and they are struggling to meet demand. It took 4 months to get these inverters. I'm still waiting on a 6 kW.
Interesting,
I haven't seen any other 12k sized 120/240 true-LF units anywhere close to this price point, with such low Idle current.
I will put them on my 'watch list' for the future 24kW system design.
Do you have the manual for the 12k? I didn't see a link to manuals on their site.
If anyone has a pair of these running together I would like to know how this worked out.
Did you connect the Genetry to Solar Assistant?
Were the installs you did using RS-232 or 485 or CAN comms?
 

"12,000W
Split Phase: 240v @ 50A (or 120v @ 50A from both L1-N and L2-N)
Single Phase: not supported. (The transformer can physically do 120v
single-phase, but none of the AC output circuitry is rated for 100A)
NOTE: Inverter alarms are based on amperage, not wattage"

OK, how much 120V single phase current CAN it do?
Oh, I think it means 50A on L1, 50A on L2, 50A on N.
Surge wattage may be available at 120V (double current), but steady state 6000W not 12000W on one phase.

"
Transfer Efficiency99% (yeah, the competition always lists this useless spec!)
AC Charge Efficiency~72% (wonder why the competition never lists this!)
Maximum Charge Currentapprox. 120A @ 48v
"

120A x 48V x (1 - 72%) = 1612W dissipated by inverter when charging?
72% is more like expected round-trip efficiency with lead-acid battery.
 
$3000 for that 12kW inverter.

Consider Sunny Island new liquidation on eBay $2000 each, pair for $4000

Or used $1200


Another used one for $1750, so a pair (used) same price as Gentry (new)

 
$3000 for that 12kW inverter.

Consider Sunny Island new liquidation on eBay $2000 each, pair for $4000

Or used $1200


Another used one for $1750, so a pair (used) same price as Gentry (new)

Don't worry, the SMA are also on my watch list!
Maybe when you get some new units you can sell me (for cheap!) your current 24kW set up! ;)
 