Texas-Mark
Solar Addict
- Joined
- Aug 4, 2021
- Messages
- 1,284
He did up in the first post.Please post the specs on your panels…
And info on the panels:
DC/Charger Volt Compatible 12v, 24v, 48v
Rated Power Output | 355 |
Voltage (VOC) | 40.6V |
He did up in the first post.Please post the specs on your panels…
Rated Power Output | 355 |
Voltage (VOC) | 40.6V |
Well… he listed the VOC, but not the vmp… I have never seen a panel rated at 12/24/48 no way a 40.6V panel can support a 48V SCC…He did up in the first post.
And info on the panels:
DC/Charger Volt Compatible 12v, 24v, 48v
Rated Power Output 355 Voltage (VOC) 40.6V
LONGI 355W LR4-HPB is a 120 cell solar panel, which combines high efficiency and low LID mono PERC cells. This module has a 35mm lightweight frame resilient enough to withstand 5400Pa load and 25mm hailstones at the speed of 23 m/s.Ok, solar panels aren’t rated that way.
Please post the specs on your panels…
DC/Charger Volt Compatible |
|
Where did you see that? Do you have more specs than what was posted earlier? I had mentioned to wire them all in parallel based on the 24V input spec listed earlier.Your charge controller has PV rated input of 70V.
It is the last number in the charge controller section of his spec he posted… VOC 70VWhere did you see that? Do you have more specs than what was posted earlier? I had mentioned to wire them all in parallel based on the 24V input spec listed earlier.
I have never seen a panel rated at 12/24/48 no way a 40.6V panel can support a 48V SCC…
It is the last number in the charge controller section of his spec he posted… VOC 70V
OP post #1Where did you see that? Do you have more specs than what was posted earlier? I had mentioned to wire them all in parallel based on the 24V input spec listed earlier.
I bought 4 Longi 355w panels
All-in-one Inverter(3000W 24V Inverter+80A controller)
Build-in 80A Controller Part
Solar Charge Mode: PWM
Rated Input Voltage: 24V DC
In any case the Voc of those panels means you cannot place them in series with that inverter's solar input Voc limit. If you are lucky the inverter's over voltage protection has saved the inverter from damage but that's no guarantee.Open Circuit Voltage: 70V
I appreciate you confirming what I have begun to suspect about the controller/inverter not being a good match. I can replace it and return thio one as long as its not damaged. Thanks for the info that I can't use that 5th panel with this inverter/controller even with them in parallel. I am copying the specs from the merchant website, so I'm not making any typos or mistakes. I can go out to the manufacturer's website to confirm them there to be sure the merchant didn't make an error.Those two specs are not compatible. A Longi 355W panel will have a Voc of ~40V and Vmp of ~35V.
If your solar controller has a maximal input voltage of 24V then you are not going to have a good outcome with those panels. Hard to know as that input voltage seems low, given inverter spec also says for solar input limit:
In any case the Voc of those panels means you cannot place them in series with that inverter's solar input Voc limit. If you are lucky the inverter's over voltage protection has saved the inverter from damage but that's no guarantee.
At best you can put them in parallel but 4 x Longi 355W in parallel is a lot of current, like about 41A at Vmp.
I'd want to validate the exact model and specifications of the inverter but I suspect the panels and inverter are a poor match.
Most likely the discrepancy in voltages is simple translation issues…Those two specs are not compatible. A Longi 355W panel will have a Voc of ~40V and Vmp of ~35V.
If your solar controller has a maximal input voltage of 24V then you are not going to have a good outcome with those panels. Hard to know as that input voltage seems low, given inverter spec also says for solar input limit:
In any case the Voc of those panels means you cannot place them in series with that inverter's solar input Voc limit. If you are lucky the inverter's over voltage protection has saved the inverter from damage but that's no guarantee.
At best you can put them in parallel but 4 x Longi 355W in parallel is a lot of current, like about 41A at Vmp.
I'd want to validate the exact model and specifications of the inverter but I suspect the panels and inverter are a poor match.
Most likely the discrepancy in voltages is simple translation issues…
It is designed for 24V batteries, and the VOC max is 70V…
The inverter looks like an Eco Worthy model. OP needs to confirm if it is, and if so this is the manual:The information provided on the all in one is not clear and confusing.
Its not surprising that the OP is having issues.
The inverter looks like an Eco Worthy model. OP needs to confirm if it is, and if so this is the manual:
Can I add the fifth panel in parallel? Can I add two more batteries.I would think the unit needs a 24v Battery to be connected so the PWM controller can function correctly, however the information provided suggests that the unit will operate without a battery.
The maximum input from the panels is 70 volts, it seems you exceeded that and may have caused damage.
The panels you have are 10 amps at 33 volts with a OC voltage of 40 volts.
Connect in parallel, this will give a maximum solar input of 240 watts per panel, 960 for the 4 in parallel, and a maximum charge current into the 24 volt battery of 40 amps.
The OPs measurements on the panels I suspect are voltage measurements.
The information provided on the all in one is not clear and confusing.
Its not surprising that the OP is having issues.
Mike
Yes. That is right. It is awkward. But I'd be confused no matter what.OP needs
The inverter looks like an Eco Worthy model. OP needs to confirm if it is, and if so this is the manual:
https://cdn.shopify.com/s/files/1/0..._in_one_inverter_instruction.pdf?v=1609313709
It makes my brain hurt the way it was written.
So, wiring just 4 in parallel will not accomplish the perhaps life saving goal of running the swamp cooler for at least 4 hours which takes 1050 watts. I need to add the 5th panel, if that isnt going to dmage the combo unit. What do you think? I don't understand all the numbers. Sorry.I took a quick look at that and here is my take.
It does need a battery to work.
The panels should be ok since it says:
"Solar panels with a maximum input voltage of 36V"
So, IMO the OPer should get his 24v battery bank, connect those. Then rewire the panels in parallel and give it a go. It will either work or not.
Thank you so much for all your time and help. I can't hook the system up in parallel till I order more cords and until I know if it's at all feasible to run the cooler for 5 hours a day without harming this inverter, I dont know if I need more cords to wire in parallel to this combo unit or if I am just having to replace it and run in series parallel with the new controller/inverter.So, wiring just 4 in parallel will not accomplish the perhaps life saving goal of running the swamp cooler for at least 4 hours which takes 1050 watts. I need to add the 5th panel, if that isnt going to dmage the combo unit. What do you think? I don't understand all the numbers. Sorry.
Maybe if I can add the second set of batteries that are coming in about a week I could charge those 4 up before 11 and get the cooler running for 5 hours.
If niether of those are a safe bet to not harm the current controller, then I'll have to look at a controller/inverter today to replace and then I would want to maximize the use of these panels. Amazon is often fast. Any guidance on specs would help.
So, wiring just 4 in parallel will not accomplish the perhaps life saving goal of running the swamp cooler for at least 4 hours which takes 1050 watts. I need to add the 5th panel, if that isnt going to dmage the combo unit. What do you think? I don't understand all the numbers. Sorry.