200A main breaker is at the main panel, no breaker at the meter?
In that case, meter gets yanked so wires aren't live during the connection.
Does SolArk have a 200A pass-through relay built in? Does it have the ability to close that relay, leaving power to house on while the rest of SolArk gets removed and shipped back for repair?
If not, would be awfully nice to have some kind of bypass/transfer switch so the lights stay on when SolArk is down for the count. But, the amount of switch gear required to send 200A straight through vs. diverting through SolArk and back will cost serious $$$.
Just a fused 200A disconnect is available. Or a new meter box with built-in main breaker. Probably less expensive than the fused disconnect!
How about instead installing a new 400A main panel with 200A main breaker? That would allow up to 200A (or more) PV breaker without violating 120% rule. But I'm not aware of branch breaker larger than 125A for consumer panels. You could have 200A main breaker at meter, 125A breaker feeding SolArk feeding existing panel, 125A breaker bypassing SolArk to an interlocked 125A "generator" breaker on existing panel.
(Maybe 2/0 cables could tap off mounting screws of 200A main breaker on new panel, feeding into 200A main breaker of existing panel, but not sure that is considered proper. More likely, two sets of 2/0 cables from fused disconnect, one set to SolArk and one to main breaker of existing panel. Sol-Ark could feed interlocked "generator" breaker of existing panel.)
You need to plan what configuration with which components, providing the functionality you want when grid is down and when SolArk is down.
If you get a design approved by permit office, mount all boxes and conduit, leave pulling wire and making connection for electrician to do while power disconnected, that is a smaller job. But conduit routing with minimal bends, thorough reaming, access to pull, is critical. Maybe you can pull yourself (2/0 is difficult!) if you can do that without risking contact to live terminals. Possibly, re-use of existing wire would minimize effort of conduit and pulling, especially if that reduces all pulling to a straight shot. Need power off for all work in that case.
Hello
My current power feed is meter outside with no cutoff switch, then a direct feed from the meter box to my main 200A breaker box.
You raise some good questions about what happens if/when the sol-ark craps out, I believe I have read that it includes a some kind of a passthrough arrangement, but it appears to be built into the box, so if the box needs to be serviced it would result in a house without power.
Best question that I currently cannot answer (thanks)
===============================================================
You need to plan what configuration with which components, providing the functionality you want when grid is down and when SolArk is down.
===============================================================
I am now thinking that perhaps some kind of manual transfer switch that would allow feed to from grid , back to main panel in basement flipped one way, then when flipped the other way would send grid power direct to the Solark 15Kw. Problem is the main panel only has one input and having two independent main feeds is not normal.
I also appreciate your suggestions about planning, and installing just the boxes/switches, and PVC conduit to reduce the size of the job.. that's good advice.
I am still struggling with the diagrams at Solark, and the suggestions (which I like) to install main power feed to the Sol-ark and skip screwing around with critical needs panels and critical needs breakers.
The images all show a 200A fused disconnect between the main feed and the solark. There is also a "line tap"
option layout , but that shows a second "critical needs" panel, so I would like to avoid that.
But I don't understand how the house will still operate if the Sol-ark goes down hard, or needs to be replaced.
I'll have to ask Solark, or perhaps someone here knows the answer.
Or maybe we just "roll the dice" and hope the solark runs perfectly for 20 years with no pause.