Huh? It has been around for over 30 years. (Edit-- actually 50 years)Since CCA is new...
I'm sure the production process is old but it's being pushed for wide application in the US in a new application (small conductors & in terminals listed for Cu + I believe exempt from explicit testing for CCA) by manufacturers & has only been in NEC since 2023 cycle. So there just aren't that many installations using it.Huh? It has been around for over 30 years.
Hi, I have 4 panels, to run 2s2p and will end up having about 15-16A at 70V to my SCC.
Would 12AWG wire CCA be ok for this? about a 35 foot wire run.
Thank you!
I have to dig out my old code books, but pretty sure it has been in the NEC since before 1990. CCA was a solution to terminal compatibility. I had it used on projects for large wire (250MCM and up), but agree the economics were never there for small wire.I'm sure the production process is old but it's being pushed for wide application in the US in a new application (small conductors & in terminals listed for Cu + I believe exempt from explicit testing for CCA) by manufacturers & has only been in NEC since 2023 cycle. So there just aren't that many installations using it.
If CCA has been used overseas with analogous terminal types, OK then (though often we do not use identical terminals to overseas).
I guess if someone installs the CCA in Al/Cu compatible connectors out of an abundance of caution it's probably no less risky than using aluminum.
But it's still experimenting for a small savings in absolute terms.
I have to dig out my old code books, but pretty sure it has been in the NEC since before 1990. CCA was a solution to terminal compatibility. I had it used on projects for large wire (250MCM and up), but agree the economics were never there for small wire.
but agree the economics were never there for small wire.
Copper cladding has some extra benefits IIRC. I think the big one was less problem losing connection integrity over time. Not an issue for compression lugs, but on small terminals it can help.For HVDC connections I think the advice is anyway to use connectors like Polaris that are dual listed so you could have already use good old aluminum if you want to save money.
Copper cladding has some extra benefits IIRC. I think the big one was less problem losing connection integrity over time. Not an issue for compression lugs, but on small terminals it can help.
I don't think I have ever seen fine-stranded aluminum though; can't imagine it working well.
Mainly because I had some laying around…Surprised to see CCA mentioned, I thought you would need to do extra work to get it still.
Since CCA is new, on top of having to size up. since it is a new product it’s quite arguably unwise to use it for solar where you want the equipment to last 20-30 years. Not enough longevity data on this thing.
I doubt you’re saving much money on a #12 35 foot run.
Why are you considering it?