fromport
Solar Addict
Afaik you can not "draw" power from a supply line hookup, **only** put power in.Buss rating is 225a. I have 125a main breaker. But if I'm line side tapped, the buss rating doesn't come into play. So I would just have a 60a breaker in the box for the inverter. Way good on 120% rule. As far as NEC goes...
And that makes sense if you follow this logic:
If your main breaker is 200 amps, and your fused disconnect the minimum 60 amps, you could pull 260 amps from the grid without any fuses triggering. But the meter socket and the wires to the transformer of your utility are only rated for 200 amps (max fuse of your main breaker panel)
Imo as soon as you install a hybrid inverter with batteries & loads, you can not hook that up to supply side.
You have to hookup the LP on the load side of the setup.