Here is the start up procedure for the 18k.
1. If equipped, turn on(close) the DC breaker between battery and inverter first. Turn on the BAT
breaker located in the cable box of the inverter and then power on the battery system.
85
2. Make sure the PV voltages of the strings are within operating parameters. Turn on(close) PV
isolator switches between the inverter and array and then on the side of the inverter.
3. Make sure Steps 1 and 2 are running properly before turning on the grid power or generator
breaker.
4. Power on the load breakers in the cable box of the inverter and then in the load panel
Before commissioning, you need to make sure that you have your connections already made. That's your solar, batteries, AC in, and AC out. Not all setups will have these, just make sure the ones that apply to you are there and connected properly.
If you have multiple units, you will want to make sure that you have all of your communication/paralleling cables connected as well. Once you power on the unit, you will need to set the master and slave inverters appropriately. This can be done from the inverter menu. I will link the manual below that goes over all of the step by step instructions on how to do this on page 28
Turning the system on before commissioning will allow you to get the wifi dongle set up. You'll need to make sure that firmware is able to be updates so that the system can be commissioned properly. If you need your firmware updated you can call Tech support, or DM me and we can set a time where I can update your firmware for you.
On page 28 of the manual, it gives you all the things to do before commissioning.
HERE is a link to the manual.
If you have any more questions about the 18kpv, please feel free to DM me. I'm here on the forum specifically to help any one that needs it.