I think I will need to read up a bit :-( Basically I want to offset one of units grid power with power from batteries to save on monthly bills.
For example, I want to run unit #2 with as much battery as possible during the day.
AC unit 2 : LRA 95, RLA 16.5
so from your statement, 16.5A * 240v = 3960w
Are these statements correct?
1) So a 6000 watt inverter should be able to handle this as long as it can start it, right?
2) And if I have 2 eg4 5k batteries, it should be able to run this for couple of hrs
3) to start the AC unit, I would need to take care of surge power which is 95A with a soft start. What do I need to get this down to run unit #2? 25A?
Thank you for all the answers..it is enlightening