Here's another quirk I've forgotten to mention.
When setting Bulk Charge V (09), (11) Float V changes as well.
You need to reset Float V (11) after setting bulk (09).
I'm frequently tweaking my float this time of year when I switch to grid to balance since PA weather has been absolutely freaking marvelous for production...
Bump up the float and hold them around 3.45V per cell, observe what the cells are doing... I bet you have runners and crawlers.
As
@Lighthouse Beacon has figured out. ?? It's a learning experience and it's freaking rewarding...
Also note that you can reduce max charging current when they start to get full... I'd bet most recently
@Kenny_ had cells running and hit HVD in his most recent User charge...when I'm charging from grid and I see cells get over over 3.4V I reduce Grid Charging Current (28). Watch the cell voltages settle when you do this... I suppose setting 10 to hold them at bulk voltage would achieve the same result.
Anyway I'm rambling. Run the system... Take some screenshots / photos when you get your cells above 3.4V, I want to see the delta...
I can't wait till summer when you guys have more power than you know what to do with and your worrying about deciding what load to run next... Water Distiller and 'mini' sauna are my go dump loads when their isn't laundry to by done.