dalemeyer22
New Member
- Joined
- Oct 1, 2022
- Messages
- 38
Doesn't look like it has a start SOC setting.What percentage do you have Start AC set at?
Doesn't look like it has a start SOC setting.What percentage do you have Start AC set at?
Start SOC is accessible from the website. It hasn't been added to the app yet.Doesn't look like it has a start SOC setting.
What are you trying to set it at? Needs to be a few % higher than your cutoff. You might be better off using charge by time. Edit: do you have free electric at night?I tried to set it and it gives me an error.
Discharge is set to 10% and was trying to set charge at the same. If I set the charge to 12% then the discharge will never reach the discharge level. Is that recommended?What are you trying to set it at? Needs to be a few % higher than your cutoff. You might be better off using charge by time.
Why do you need to AC charge?Discharge is set to 10% and was trying to set charge at the same. If I set the charge to 12% then the discharge will never reach the discharge level. Is that recommended?
LolWhy do you need to AC charge?
Is your electric free at night? (Somebody has free electric at night)
One of the other settings maybe conflicting.BTW, also tried setting to 20% and still get the error.
which firmware are you running on your 18Kpv?I changed the AC Charge Based on to (SOC/VOLT) and still same error when trying to set start SO
which firmware are you running on your 18Kpv?
fAAB-0C0D |
I'd update firmware. charge by SOC wasn't officially added until 1010
fAAB-0C0D
Yup, that would do it. Ok thanks. I greatly appreciate you help on this!I'd update firmware. charge by SOC wasn't officially added until 1010
FAAB-1010
2023-06-30
- Changes log (Same as fAAB-1010/ eAAB-1010/EAAB-1010)based on FAAB-0D0E.
- 1. Enlarged the grid sell back power limitation ,if power limitation is high than 200% , then real limitation will be 1000% max.
- 2. Peak-shaving logic optimization.
- 3. Fortress battery protocol optimization :working in leadacid mode where is communication failure issue.
- 4. AC Charge according to SOC or VOlT could be supported in this firmware version .
- 5. Octopus charge function is supported.
- 6. To avoid relays clicking on and off frequently due to grid fluctuation, a return value has been added in this firmware version .
- 7. Hina battery protocol is supported in this firmware version.
- 8. Grid regulation changes :Hawaii changed to HECO , and added KIUC grid regulation.
- 9. Battery capacity could be showed in the LCD display .
- 10. Optimization on AC coupling function : AC charge and battery discharge will be seamless switching way .
- 11. Fans control logic optimization to reduce fans noise
Looks like only one part of the update went through. "OC" is still old. It's typically a two part update.Ok, updated but i had to set a time for it to start charging automatically. Even though i can set it to SOC on the website it still wont stick or let me set the Start AC Charge SOC%. Only works with time based.
Firmware is: 0C12
Next version is 1616 but not a "standard update" so will require siginture to apply the update, i think.
DM @Markus_EG4 he should be able to help.Ok, updated but i had to set a time for it to start charging automatically. Even though i can set it to SOC on the website it still wont stick or let me set the Start AC Charge SOC%. Only works with time based.
Firmware is: 0C12
Next version is 1616 but not a "standard update" so will require siginture to apply the update, i think.
Ok I will, thanks.DM @Markus_EG4 he should be able to help.