I believe the GW unit offers that, see below:As I stated before, how to automatically turn on the generator will be up to you to figure out. I'm not aware of any function in a GW inverter that will do this.
Just to be on the same page, if I do remove N-G bond from existing cabin electrical panel and I add a new panel inside the shed, I would need only grounding rods by the shed. Is this correct?You need a properly sized breaker ahead of the GW unit. That is why you need a breaker panel in the shed plus it allows N-G bond to be there which is close to source.