I’m toying with the idea of combining 2 or 3 panels before feeding into a high-capacity Microinverter and have some newbie questions about wire size and fusing.
I know that 3P generally requires a fuse on each incoming branch/panel while 2P does not and I just want to confirm the logic for that again.
The concern is a short in the panel itself, not the panels lead-in wires, correct?
A short in the panel can draw 2 x Isc from the other 2 panels + Isc from the shorted panel so total current at the point at the location of the short can be as much as 3x.Isc.
Am I correct that that is the concern?
Or is it more generally that the panel output wires are only rated for 1x Isc which can never be exceeded by a short within the panel at 2P but can draw 2 x Isc through those wires at 3P?
And my second question has to do with PV wire sizing and chassis wiring limits versus power transmission limits.
For a free-standing wire from a battery to an inverter, chassis wiring limits apply, so wouldn’t that be the case for a short free-standing wire within a PV array such as an MC4 ‘Y’ cable?
The Y cables I am considering are 12AWG PV wire and state that they are rated for up to 35A maximum on the common output.
12AWG is limited to 9.3A for power transmission but 41A for chassis wiring: https://www.powerstream.com/Wire_Size.htm
So is 41A the correct limit to use for a short length of 12AWG wire freestanding within a solar array (appropriately de-rated)?
If I’m understanding all of this correctly, the MC4 inline fuses are expensive enough that 2P strings may be the only option that makes sense…
I know that 3P generally requires a fuse on each incoming branch/panel while 2P does not and I just want to confirm the logic for that again.
The concern is a short in the panel itself, not the panels lead-in wires, correct?
A short in the panel can draw 2 x Isc from the other 2 panels + Isc from the shorted panel so total current at the point at the location of the short can be as much as 3x.Isc.
Am I correct that that is the concern?
Or is it more generally that the panel output wires are only rated for 1x Isc which can never be exceeded by a short within the panel at 2P but can draw 2 x Isc through those wires at 3P?
And my second question has to do with PV wire sizing and chassis wiring limits versus power transmission limits.
For a free-standing wire from a battery to an inverter, chassis wiring limits apply, so wouldn’t that be the case for a short free-standing wire within a PV array such as an MC4 ‘Y’ cable?
The Y cables I am considering are 12AWG PV wire and state that they are rated for up to 35A maximum on the common output.
12AWG is limited to 9.3A for power transmission but 41A for chassis wiring: https://www.powerstream.com/Wire_Size.htm
So is 41A the correct limit to use for a short length of 12AWG wire freestanding within a solar array (appropriately de-rated)?
If I’m understanding all of this correctly, the MC4 inline fuses are expensive enough that 2P strings may be the only option that makes sense…