Yes..... but the requirement has nothing to do with the fuses. The fuses are there to protect the panels on that string. They are not there to protect the output circuit. The NEC wants the wires for the output circuit to handle 1.56 the Imax, where Imax is the sum of the Iscmax of all the parallel strings. With this gauge wire, a short on the output circuit could sit there all day and not cause a fire (and not blow the string fuses)So with 3 incoming 15A fuses rated at 90C, the outbound wire needs to be rated for at least 45A, correct?
Correct, but as with the wire, it is not related to the fuse.But the question of overall triple Y-connector rating remains: if rated for 45A it would be safe protected by 3 15A fuses and if only rated for 40A, it would not (at least according to NEC), correct?
Got it, sorry. So with a 90C rating, it just means an additional safety factor.
Got it - thanks for explaining. So in that case, it means the outbound wire needs to be rated for 3 x 156% x 9.29A = 43.55A, not 3 x 15A = 45A, correct?Yes..... but the requirement has nothing to do with the fuses. The fuses are there to protect the panels on that string. They are not there to protect the output circuit. The NEC wants the wires for the output circuit to handle 1.56 the Imax, where Imax is the sum of the Iscmax of all the parallel strings. With this gauge wire, a short on the output circuit could sit there all day and not cause a fire (and not blow the string fuses)
And so the double-Y which does not require any fusing will be fine with a 2P1S string of my panels because the output only needs to be rated for 2 x 156% x 9.29A = 29.03A, we’ll below their output rating of 40A (10AWG),Correct, but as with the wire, it is not related to the fuse.
CorrectGot it - thanks for explaining. So in that case, it means the outbound wire needs to be rated for 3 x 156% x 9.29A = 43.55A, not 3 x 15A = 45A, correct?
Can’t believe it’s taken me 2-1/2 months to circle back to this idea, but I now have a different array I’m planning where a 3P string of different panels I just acquired is once again attractive and would appreciate a reality check from you that I’m understanding everything correctly:Correct
I am struggling to understand the description of the system.Isc @ 50C = 8.782A so need 15A fuse on each panel
Our earlier discussion was about a 1S3P string and I should have stated that again instead of just saying ‘3P’ assuming you’d remember our earlier discussion.I am struggling to understand the description of the system.
Note: I can't tell how many panels are on each of the 3 parallel strings, but for calculating the wire and fuse sizes it does not matter how many panels there are. It could be 1 panel per string or 10 per string. The current calculations are the same.
A 3 string array of panels with panel ISC of 8.782A would look like this with in-line fuses and Y connectors:
View attachment 123605
The same array with a combiner box might look like this:
View attachment 123604
Note that there is only one fuse per string.... no matter how many panels are on the string.
Does this help?
OK. That does not change the current calculation.So my 3-panel string looks like your first picture where each of the 4 panels in series is reduced to just a single panel.
I’m charging a 24V battery with a 1S array, so voltages are low and currents are high.
Voc = 37.5V @ 25COK. That does not change the current calculation.
View attachment 123659
What are the Voc and Vmp of the panels?
My Epever SCC has an MPPT range starting at Vbat + 2V.Most charge controllers need 4 or 5 volts above battery voltage just to turn on. That means the panel Vmp should probably be at least 36V for a LiFePO4 battery (Preferably a few volts higher). You might get away with Voc of 36V, but that would be pushing it, Particularly on hot days.
You are a fantastic asset to this Forum!Is this the set-up?
View attachment 123669
The 6AWG part of the output circuit will be OK.
The 10AWG part of the output circuit is marginal. If you go strictly by the NEC chart, 10AWG should not be used for 41.1A even for 90C rated wire. (The limit is 40A for 90C wire.) 8 AWG would be fine.
My 6AWG home run wires are in conduit (3-conductors per conduit), so I should apply the NEC code.View attachment 123667
However, if you go by the standard used in boating you are probably OK
View attachment 123668
YesIf I combine the two 6AWG circuits in the DC breaker box after the 2 50A breakers / switches, I just need to assure I’m using wires rated for at least 82.4A from the DC breaker box to the SCC, correct?
Hmmmmm. There may be a problem with thisI can make 2 parallel runs of 6AWG down to the basement so I can install 2 completely parallel output circuits as you have pictured above.
I obviously could connect those two output circuits to two I depend and SCCs but I am hoping to connect them to a single SCC.
Thanks, but do you agree with my assessment that since the SCC is limited to 1500W of input power at a minimum input voltage of at least 22VDC, 68.2A is the maximum input current I need to assure my wires from DC breaker box / combiner to the SCC are rated for (meaning 6AWG wires and not 4AWG wires will suffice)?
If I understand the question.... Then NO. Everything before the SCC must be rated for the full 82.2A.Thanks, but do you agree with my assessment that since the SCC is limited to 1500W of input power at a minimum input voltage of at least 22VDC, 68.2A is the maximum input current I need to assure my wires from DC breaker box / combiner to the SCC are rated for (meaning 6AWG wires and not 4AWG wires will suffice)?
This is precisely the sort of issue I was hopping you might help me discover before I committed to my plan.Hmmmmm. There may be a problem with this
View attachment 123706
Technically, this is a 1S 6P arrangement with very distributed interconnects. If there is a short on the 10AWG wire, it would need to withstand all 82.2A.... and 10AWG will not be able to handle it.
However, if each set were on a separate SCC, it would be two separate PV systems and each one maxes out at 41.1A.
The fact that my 1500W @ 24V SCC only accepts a maximum of 6AWG on both input and output wires makes me suspect they have a different interpretation…If I understand the question.... Then NO. Everything before the SCC must be rated for the full 82.2A.
The reason for this is that the PV circuit is designed to be able to handle a short without burning up and without an over-current device popping.
Let's imagine there is a short right at the SCC input. In this case, all of the current from all of the panels will be going through the short.
However, it *is * reasonable to use the limits of the SCC when sizing the output wires of the SCC.
It is hard to say. I tend to worry about that kind of thing. Others don't.Is a short between PV wires really a realistic risk-case?
For example, if I installed a 50A blocking diode between each 6AWG string and the 60A DC breaker, wouldn’t that protect against the very unlikely even if a shirt between 10AWG + and - wires?
Blocking diodes rated for over 42.2A will dissipate ~20W and will drop string voltage by ~0.5V but should protect against this risk you’ve pointed out, correct?
If you’re convinced this is a potential risk I should protect against, I take that input seriously and will adjust my plan accordingly.
It is time for me to speak up about EPever. I am *really* not a fan of EPever. I had one that died. At first, I just thought I was just unlucky but then I started seeing other folks that have had problems with EPever. Some folks have seen problems where the unit would stop working till they totally disconnected it and reconnected it.... It would start working again for a while and then they would hit the problem again. It seemed like they were most likely to hit the problem when the controller was operating at max capacity.... and that is what you are planning to do.The fact that my 1500W @ 24V SCC only accepts a maximum of 6AWG on both input and output wires makes me suspect they have a different interpretation…
I’ll take my time to understand this issue before committing to purchasing my new SCC(s).
Their 40A SCC also accepts 6AWG, so two of those in parallel would be one solution.
Their 80A SCC accepts 4AWG but costs 3 times their 40A SCC, so your slowly steering me away from the idea of one SCC for the full 6P1S string towards getting a separate 40A SCC for each 3P1S string…
Their 30A SCC is ~15% cheaper but only accepts a maximum of 8AWG, so probably not worth considering (especially when considering that it’s always to use an SCC below maximum ratings).