MrM1
I'm Here, But I'm Not All There
I have 2 48v 280ah DIY batteries. System has been up and running for several months no problem. The entire system (except Solar panels) is mounted in a cargo trailer and today, out at the farm, them moved the trailer. After powering everything down, moving the trailer, then powering everything up, the system seemed to work. Then 10 min later it did not.
In testing, both of my 225 amp Class T fuses (one on each battery bank) were blown. Because I was not on site, I do not know what they did other than move the trailer. As far as I know 400 amp main fuse (see diagram) is not blown.
What could have caused the 2 Class T Fuses to blow after the system has been up and running for several months?
Could it be that I used a fuse that was too small at 225a?
What should I be testing / looking for before installing new fuses?
Set up:
- 48v system
- 16 EVE 280 ah cells in 2 banks parallel (32 cells total)
- 225 amp fuse on each battery bank (x2)
- 200amp JK Heltec BMS on each battery bank (x2)
- 400 amp main fuse before inverter (x1)
- Cable from batteries to parallel busbar = 00
- Cable from busbar to inverter = 0000
- Growatt 12k AIO inverter with pre-charge resistor switch
- Victron Smart Shunt before the 400 amp fuse
As installed x2
Diagram
In testing, both of my 225 amp Class T fuses (one on each battery bank) were blown. Because I was not on site, I do not know what they did other than move the trailer. As far as I know 400 amp main fuse (see diagram) is not blown.
What could have caused the 2 Class T Fuses to blow after the system has been up and running for several months?
Could it be that I used a fuse that was too small at 225a?
What should I be testing / looking for before installing new fuses?
Set up:
- 48v system
- 16 EVE 280 ah cells in 2 banks parallel (32 cells total)
- 225 amp fuse on each battery bank (x2)
- 200amp JK Heltec BMS on each battery bank (x2)
- 400 amp main fuse before inverter (x1)
- Cable from batteries to parallel busbar = 00
- Cable from busbar to inverter = 0000
- Growatt 12k AIO inverter with pre-charge resistor switch
- Victron Smart Shunt before the 400 amp fuse
As installed x2
Diagram