My main panel is just a single row of breakers. No way to put another across from the bottom one.
And I could not meet the 120% rule with my A/C feed as it requires a 40 amps breaker. The start surge on that beast is 105 amps. That is the main reason I just can bring myself to put it in the backup loads panel. That is well beyond the rating of the transfer relays in the XW. And the maximum short term current in off grid mode is just 51 amps for 1 minute. Even with a soft start kit, I don't think it could crank it up.
Yes, there is a Square D brand knife switch disconnect that cuts off the entire Enphase system. If I add Enphase inverters, my original plan is to put them into the Envoy on a second array breaker. My backup loads panels is way below spec, so there is no issue putting a 30 amp back feed breaker in there. The XW is feeding the other end of the buss bars in the backup loads panel with another 30 amp breaker. So that is a total of 60 amps of feed into a 100 amp rated panel.
The grid side of the XW is on the 20 amp back feed breaker in my main panel. This is my "weakest link". It is easy to make the XW limit to not exceed 16 amps going back, and it even knows how much it can add to the export coming from the Enphase AC coupled inverters, so even if I command it for 16 amps of back feed, it will only back feed 5 amps, if the Enphase is already pushing back 11 amps. The 2 problems are that it can't limit the Enphase back feed, and if the loads draw more than 20 amps, where is the extra power going to come from?
As long as the battery is not full, it limits the back feed by stuffing the extra energy into the battery.
As long as there is enough energy in the battery, it limits the draw from the grid input by using power from the battery.
But we don't have unlimited battery capacity. I need a backup plan for those few times where the battery is not able to handle enough to limit the grid side power.
And I could not meet the 120% rule with my A/C feed as it requires a 40 amps breaker. The start surge on that beast is 105 amps. That is the main reason I just can bring myself to put it in the backup loads panel. That is well beyond the rating of the transfer relays in the XW. And the maximum short term current in off grid mode is just 51 amps for 1 minute. Even with a soft start kit, I don't think it could crank it up.
Yes, there is a Square D brand knife switch disconnect that cuts off the entire Enphase system. If I add Enphase inverters, my original plan is to put them into the Envoy on a second array breaker. My backup loads panels is way below spec, so there is no issue putting a 30 amp back feed breaker in there. The XW is feeding the other end of the buss bars in the backup loads panel with another 30 amp breaker. So that is a total of 60 amps of feed into a 100 amp rated panel.
The grid side of the XW is on the 20 amp back feed breaker in my main panel. This is my "weakest link". It is easy to make the XW limit to not exceed 16 amps going back, and it even knows how much it can add to the export coming from the Enphase AC coupled inverters, so even if I command it for 16 amps of back feed, it will only back feed 5 amps, if the Enphase is already pushing back 11 amps. The 2 problems are that it can't limit the Enphase back feed, and if the loads draw more than 20 amps, where is the extra power going to come from?
As long as the battery is not full, it limits the back feed by stuffing the extra energy into the battery.
As long as there is enough energy in the battery, it limits the draw from the grid input by using power from the battery.
But we don't have unlimited battery capacity. I need a backup plan for those few times where the battery is not able to handle enough to limit the grid side power.